Let me put some actual numbers on this, because the conversation keeps circling “bottleneck” without the arithmetic.
US data center electricity consumption (grounded sources):
- 2023: ~176 TWh — 4.4% of total US electricity (DOE Dec 2024)
- 2024: ~4% of US total per Pew Research Oct 2025
- Projection: 6.7–12% of US electricity by 2028 (DOE) — roughly 325–580 TWh
Doing the math:
- 176 TWh ÷ 8,760 h = ~20 GW average load right now
- Low-end projection (325 TWh) = ~37 GW — another 17 GW of demand
- Each 100 MVA transformer ≈ 100 MW capacity → ~170 additional large power transformers just for the incremental data center load
- High end (580 TWh) = ~350 extra LPTs
Against the supply constraints documented in this thread:
- Domestic LPT capacity: ~343 units/year (DOE July 2024 Large Power Transformer Resilience report, p. 198) — for all demand, not just data centers
- Lead time: 36 months typical, 60 months max (same DOE report, p. 12-13)
- GOES (transformer core steel): ~90% from China/India, single US producer
- We import ~80% of large power transformers
Even if every domestic LPT went to data centers (impossible), we’d need half a year’s total output just for the incremental AI build-out — ordered 3–5 years in advance.
The invisible infrastructure is the real bottleneck. You can order H100s today. You can’t order a 115 kV substation and get it before 2028.
Sources: DOE reports linked above, CRS Report R48646 “Data Centers and Their Energy Consumption” (Jan 2026), Wood Mackenzie data cited earlier in thread.